geordi wrote:
In the local mechanic's defense, you can't really check for leaks if there isn't any coolant in the system to check with. At a local shop that I have been to in Florida, (and is VERY busy most of the time) their policy is to check / charge the system first, and look for leaks then with a chemical sniffer. The second option for places that might not have the business to justify a $$$$$ sniffer tool is to charge it up with the UV dye. Either way - Give the system something to leak out, then find that leak.
Not true. One method as you have noted is to use a refrigerant sniffer. Second as mentioned is the UV dye.
Another method to include as noted above is to use nitrogen....which should be
dry nitrogen. You do not want to introduce any moisture and/or non-condensibles into the system at all. Do not use compressed air! Of course you need to use a proper pressure regulator and understand what the safe working pressure of your system is so that you do not overpressurize it.
Dry nitrogen is also used to break a vacuum on systems exposed to long periods of moisture.
Lastly, any system that is leaking will not hold a vacuum for any significant period of time. The only way to know for sure is by using a vacuum gauge that measures in microns.